Maybe you lost a phase in your Main circuit panel? If all circuits on one side are dead, that would indicate a lost phase.
Single phase 120 residential. Have power to two outlets, but nothing past, which includes lights for master bedroom and my sons entire room. Found an open on the hot wire between last outlet with power and next outlet. So feeling I will have to open up the wall to run new romex
 

Redz72

Ram Guru
Joined
Jun 1, 2023
Messages
1,152
Reaction score
2,279
Location
Langhorne, PA
Single phase 120 residential. Have power to two outlets, but nothing past, which includes lights for master bedroom and my sons entire room. Found an open on the hot wire between last outlet with power and next outlet. So feeling I will have to open up the wall to run new romex
Could just be a bad/old receptacle. Maybe the load side terminals are shot? It’s worth swapping out the receptacle before opening the walls. But good luck either way. I enjoy electrical work, but chasing ghosts is not fun.
 